    Default Tankless Water Heater For Floor Heat

    Anybody care to share information about using the new style tankless water heaters for floor heat? I need to replace my old Jarco 350K btu money pit with something new and more energy efficient.

    I’ve been doing some extensive research and comparing different demand heaters, Takagi, Paloma, Rinnai to name a few. Some are condensing units and some non-condensing. The non-condensing are usually about 84-85% efficient and the condensing units are 94-98% efficient. The condensing units can be vented using PVC while the less efficient units need to be vented using stainless steel vent pipe with a condensation drain added to the vent stack which is more costly.

    Some of the heat exchangers are copper and some are Stainless steel and copper. The condensing units usually use stainless and copper.

    The problem I’m having is trying to determine what will work and how well it will hold up running Polyethylene Glycol in the system. Most of these demand heaters are manufactured for heating “Water” and don’t offer details or suggestions when using them in hydronics or snow melt systems which is basically what we have.

    I have my eye on this model after doing some research…It’s the Paloma PHH-32RDV. It’s a condensing boiler with a 94% efficiency rating. It has a copper/Stainless steel heat exchanger, 199,999 btu rating, can be vented using PVC, has a direct vent cold air intake, and can heat water +35° at 9.5 GPM and 77° at 4.9 GPM Temperature rise.

    What are the pro’s and con’s of using a heater/boiler like this? This one is realitively inexpensive compared to “Boilers” on the market. The one I mention can be bought for less than $1300 which is considerably cheaper than the Takagi TM32 commercial that only uses a copper heat exchanger and has to be vented using Stainless Steel Pipe. I know some of you are using these demand heaters for floor heat. So tell us what model your using, why, and how well its working for you. Thanks!

  2. The Following User Says Thank You to 2Biz For This Useful Post:

    Bubbles Galore (10-10-2012)

  3. #2
    Join Date
    Dec 2007
    Location
    Pittsburgh, PA
    Posts
    936
    Thanks
    21
    Thanked 38 Times in 37 Posts

    Default

    This website should be a great help. It shows plumbing of radiant floor heat using a on demand heater:

    http://www.radiantcompany.com/heatso...hematics.shtml
    www.carwashbusiness101.com "Newbies Start Here"

  4. The Following User Says Thank You to Buzzie8 For This Useful Post:

    Bubbles Galore (10-10-2012)

  5. #3
    Join Date
    Sep 2007
    Location
    Fargo,ND
    Posts
    1,009
    Thanks
    4
    Thanked 43 Times in 40 Posts

    Default

    Those are nice diagrams. I just bought a Lochinvar 199K 96%
    eff. boiler from carwashboilers.com Not sure if this makes a difference,
    but every 2 years we have the boiler inspector stop by. $35 to the state,
    and the inspector is sent by my insurance co. They test the low water
    cutoff, and the overpressure valve. I know the palomas shut off when
    out of water, but not sure if it would meet our states specs, like the
    other boilers. I bought the boiler for $4200, and found a hvac guy to
    do the complete install in a couple weeks- plumbing, gas, and electrical
    changes plus drill a 4in hole thru concrete for the single intake and
    exhaust. Just 4 to 5 hours at their rate plus materials they figured.
    Am I missing the obviously cheaper way to go. Why should i spend
    more for about the same?

    http://www.carwashboilers.com/knight...y-boilers.html

  6. #4
    Join Date
    Sep 2007
    Location
    North Dakota
    Posts
    1,199
    Thanks
    23
    Thanked 43 Times in 42 Posts

    Post Something to consider

    Most people are not aware that more glycol causes a loss of heat transfer with the same input BTU expenditure. I myself was surprised when I first saw a mechanical engineering trade journal article showing the proof etc. a few years ago.

    Something to consider ... especially the potentially more harsh winter areas & the more dense the glycol needs to be.

    At our place we have just boiler water in the main boiler setup. That way at the point of combustion it is more efficient. From there we use Spirec heat exchangers to circulate the boiler water on one "in & out" of the Stainless Exchanger & the glycol on the other "in & out". I did get help from a mechanical engineer back in about 1991 or so for the original setup on the design. We don't regret having gone with that approach. Here is a link to the Spirec website.

    http://www.spirec.com

    mike

  7. #5
    Join Date
    Nov 2010
    Location
    Ohio
    Posts
    1,013
    Thanks
    140
    Thanked 128 Times in 121 Posts

    Default

    The more I research this the more issues I'm finding that needs to be overcome. The glycol being one of them. It consumes about 10% of the total BTU output. Another issue I see with the Demand Style Wall heaters is the amount of Head Pressure you need to overcome in the unit itself to produce the rated flow. Let alone the head pressure in the zones. The Takagi T-H2-DV-NG 199K BTU Condensing boiler adds 110 feet of head pressure in the unit itself at the rated 9 gpm flow rate. It would take more than a Taco Stye pump to produce the PSI to obtain the rated flow.

    This is not going to be as easy as I had thought. Theres a lot more to it than putting a Taco pump between the boiler and manifolds. There are diagrams out there that shows it can be done. I'm not giving up yet...

    Thanks for the Input so far.

  8. #6
    Join Date
    Nov 2010
    Location
    Ohio
    Posts
    1,013
    Thanks
    140
    Thanked 128 Times in 121 Posts

    Default

    Quote Originally Posted by Buzzie8 View Post
    This website should be a great help. It shows plumbing of radiant floor heat using a on demand heater:

    http://www.radiantcompany.com/heatso...hematics.shtml
    Thanks for the link! Although I already found it and studied it hard! In the list of Schematics/Photos, the one labeled "A 2-zone CLOSED system" comes closest to what I need to put together. I believe this is called a Primary and Secondary loop system. This way one pump takes care of the boiler and one pump (or however many you want) takes care of the zones. I need to call Takagi and see what size pump is required just for the boiler.

    I found (2) pulications online for snow melt systems that might be of use. I uploaded them to my server for download. There is some good information about how to size a system for snow melt. Basically what we're trying to accomplish.

    http://bcoweb.com/photos/Viega_Snow_Melting_System.pdf

    http://bcoweb.com/photos/CPS_Snowmelt.ppt

    Addining another useful link...

    http://www.radiantcompany.com/manual/index.shtml
    Last edited by 2Biz; 10-12-2012 at 03:04 AM.

  9. #7
    Join Date
    Aug 2007
    Location
    Tri-Cities, WA
    Posts
    3,692
    Thanks
    27
    Thanked 102 Times in 77 Posts

    Default

    You will need a multistage pump
    Vice President of everything & the Janitor


  10. #8
    Join Date
    Nov 2010
    Location
    Ohio
    Posts
    1,013
    Thanks
    140
    Thanked 128 Times in 121 Posts

    Default

    I called Tech support at Takagi and he said a Taco 009 SS pump is what they recommend to supply water/glycol to the boiler. 10 gpm and 35 feet of head pressure. This is just for the boiler. You need another pump for the loops.

    This diagram (Attached) is about as simple as you can get. It is all you need for Snow Melt and when using a Condensing-Modulating Boiler.

    http://bcoweb.com/photos/piping schematic.pdf

  11. #9
    Join Date
    Sep 2007
    Location
    North Dakota
    Posts
    1,199
    Thanks
    23
    Thanked 43 Times in 42 Posts

    Post

    Quote Originally Posted by 2Biz View Post
    I called Tech support at Takagi and he said a Taco 009 SS pump is what they recommend to supply water/glycol to the boiler. 10 gpm and 35 feet of head pressure. This is just for the boiler. You need another pump for the loops.

    This diagram (Attached) is about as simple as you can get. It is all you need for Snow Melt and when using a Condensing-Modulating Boiler.

    http://bcoweb.com/photos/piping schematic.pdf
    2Biz,

    I wonder if the following unit's own built in circulator would mean the unit's circulation would be taken care of ... eliminationg the need to buy a Taco 009 pump?

    http://www.globalindustrial.com/p/pl...ni-buffer-tank

    mike

  12. #10
    Join Date
    Nov 2010
    Location
    Ohio
    Posts
    1,013
    Thanks
    140
    Thanked 128 Times in 121 Posts

    Default

    Looks like a nice unit and comaparable to the Takagi T-H2-DV-ng or the new style T-H3-DV...The Takagi has slightly higher ratings...6.1 GPM @ 60° temp rise and 5 GPM @ 75° temp rise compared to the Navien's 5.8 GPM @ 50° temp rise. It does have a nice feature, dual SS heat exchangers. The Takagi only has a Primary SS heat exchanger and copper secondary.

    I downloaded the Navien's manual and it didn't have anything listed on the pump specs. So I can't help you with that. But you might want to take a look at the diagram in this brochure on the plumbing hookups. It has a hot outlet and hot return along with a cold water inlet. Different than the Takagi which only has a cold intake and hot outlet. Here is the link to the brochure:

    http://www.navienamerica.com/PDS/ftp...RNP_120823.pdf


    I don't know how you would plumb this model with the internal pump and having the "Hot" circulation loop with the single cold inlet....I would call Tech Support to see how that works.

 

 
Page 1 of 9 1 2 3 ... LastLast

Similar Threads

  1. On demand water heater for floor heat
    By sparkey in forum General Discussions
    Replies: 14
    Last Post: 01-02-2011, 05:20 AM
  2. Tankless water heater for SS soaps?
    By AdamA in forum Self Serve Washes
    Replies: 9
    Last Post: 12-07-2009, 01:18 PM
  3. Tankless Heaters for Floor Heat
    By Bubbles Galore in forum Self Serve Washes
    Replies: 5
    Last Post: 06-09-2009, 02:19 AM
  4. Tankless Raypack floor heater
    By Eric H in forum Self Serve Washes
    Replies: 18
    Last Post: 01-31-2009, 08:25 AM
  5. Tankless Water Heater Owners
    By ibspuds in forum Self Serve Washes
    Replies: 7
    Last Post: 01-30-2008, 07:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
 

Subscribe Today!

Self Serve Carwash News is back! Forum users who subscribe before

December 15th can get a 33% discount off the regular price by

entering the promo code: “glad”


Click http://www.sscarwashnews.com to subscribe!

Click X to never see this pop-up again.