When either the Tire Cleaner, PreSoak, or Foam Brush functions are chosen in the bay nothing turns on. I have Ginsan equipment. I swapped out the metering box door and I'm still having the same problem.
In the mechanical room, all three lights light up at the same time (Tire Cleaner, PreSoak, or Foam Brush) on the pump stand. Any help is appreciated!
Thanks,
Keith
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,938
Points
113
Location
Texas
Does it have the logic module in the electrical box above each pump?
 

ClassicsCW

New member
Joined
Sep 25, 2011
Messages
6
Reaction score
0
Points
1
Location
Holland, MI
It's definately not a rotary switch problem ( cuz it a button door) And I totally replaced the door with a new one and had the same problem.
Above the pump there is a GS-22 and the GS255 (Counter). I'm not sure what the GS-22 does.
 

2Biz

Thread Killer!
Joined
Nov 22, 2010
Messages
2,795
Reaction score
409
Points
83
Location
Ohio
Do you know how to use a voltmeter? Your problem could be very difficult to diagnose given the infinite possibilities. Since your solenoids aren't energizing, can't you work backwards from the solenoids and check each component for input and output voltages when a given function is selected? Surely you can find the culprit. Doing this will also help find broken/cut wires if that's the problem.
 
Joined
Nov 9, 2007
Messages
330
Reaction score
1
Points
16
Location
CT.
The GS-22 is used to energize the trickle sol to kill the weeps when a low pressure function is selected that uses weep, and i think it also is tied into the low water cut off.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,938
Points
113
Location
Texas
The GS-22 is used to energize the trickle sol to kill the weeps when a low pressure function is selected that uses weep, and i think it also is tied into the low water cut off.
If the GS-22 fails it can cause a short and act like what was described in the first post.
 